Is there any specific required performance for the blower door test in terms of cfm/sf of envelope or ACH?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium forForum discussion
Air Sealing Guidance for LEED BD&C IEQp2
Is there any specific required performance for the blower door test in terms of cfm/sf of envelope or ACH?
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Ben Stanley
Senior Sustainability ManagerWSP - Built Ecology
LEEDuser Expert
250 thumbs up
June 6, 2017 - 11:45 am
Hi Gustavo,
I may not understand your question exactly but the performance requirement is expressed in leakage area (1.25 square inches) per enclosure area (100 square feet). Are you looking to see if there's a way to convert that metric into ACH? If so, I'm not aware of an equivalent expression of the performance metric in ACH or cfm/sf.