FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Big Ceiling Fan

I have a job where there are several Big Ass Fans. My problem is in determining how to model them in the energy simulation. First, since HAP is being used, and there isn't anything to help lower the heating and cooling requirements, I'm pretty sure that it is just ignored. Please tell me if I'm reading ASHRAE 90.1 correctly on this one. Second, I'm pretty sure that modeling it as a separate entity with it's own schedule and power is required, but am not sure if it should be a process load or not. I'm fairly certain it's not a process load, but am looking for some help to make sure that I'm looking at this correctly. Thank you,

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sun, 08/04/2013 - 22:56

I think it is a process load. Since it does not affect ambient temperatures in the space like a heating or cooling system, it is basically a motor load producing heat in the space. In general ceiling fans do not impact space temperatures but do affect thermal comfort by increasing the cooling effect through air movement. How it will be operated would dictate whether it needs a separate schedule or can be placed on another, already existing schedule. You do need to model it just like every other load which affects energy use.