FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

A portion of our building envelope is historic. Can we exclude it from our model?

Our project has a diesel backup generator. Should we include it in our energy model?

For an existing building, do I need to rotate the model?

Can SHGC be higher in the proposed than in the baseline model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Do I need to justify the electrical and fuel rates I am using in my model?

Our process load is higher than 25%. Do we have to justify that?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Below Grade Garage Exhaust with CO Monitoring

Condition: I have a completely unconditioned garage located in the cellar. There is no heating. No cooling. Only an exhaust fan and an opening in the entry gate to the garage to provide unconditioned fresh air. This garage fan operates via VFD as there are carbon monoxide monitoring controls that allow fan speed to modulate based on those levels. I am NOT modeling this as a system as I am not required to given the fact that there is no cooling or heating (unconditioned spaces have neither heating nor cooling systems). The exhaust CFM and the fan power remains the same (as shown in the design dwgs) in the baseline and proposed cases. The only difference is that fan operating schedule: baseline is 100% on during occupied hours and the proposed case fluctuates based on a similar type of people schedule throughout the day. The LEED reviewer has indicated this as a DCV system (?!) and has noted that I should be treating my exhaust fan according to the baseline fan power calcs AND the ASHRAE minimum ventilation rates. The reviewer is treating my system as DCV even though the ASHRAE application of DCV applies to CO2 sensors and modulating occupancy, not CO (related to toxins in the air; as a result of increased intermittent occupancy). In my opinion, this should be treated as an exceptional calc following the method I described earlier because fans that ventilate only, ie garage exhaust fans, are NOT qualified as a fan system, meaning that the fan power remain equal in both modeling cases. Additionally, the rules for modeling DCV do not apply in this case, for the reasons listed above. Please let me know your thoughts.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 09/28/2012 - 19:08

Same as the answer further on in the string. Technically it is a DCV as I understand the term but demand here is cars, not people. Sounds like you are using people as a proxy for cars. It is definitely an exceptional calculation. You can find good guidance regarding garage usage in one of the ASHRAE Handbooks (can't recall which one right now). You will need to make sure this is not a local requirement (if it is you can't claim savings) and provide a good justification for the schedule you are using. The Baseline fan volume should not exceed the minimum required ASHRAE 62.1 parking ventilation rates of 0.75 cfm/square foot. The Baseline fan power should be the same as the Proposed (unless you are using premium efficiency motors then the Baseline fan power can be a bit higher based on standard motors). I agree that G3.1.2.9 does not apply to this ventilation only system.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.