The project I'm working on currently is for a production plant and office zones all in one building. There is no cooling coils in all designed system with the exception of the Dx unit in the server room. All systems are Ventilation and heating. The question is related to the system in the Baseline model. There are allowed heating only systems when it is for stores, stairs, technical rooms, etc. In my case however the office zones are also designed as Heating only (ventilation and aux radiator heating). Should this be modeled in the Baseline also as the other heating only systems, regarding that it is for office areas. Thanks.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
An older thread
https://leeduser.buildinggreen.com/forum/energy-modeling-unconditioned-human-occupied-spaces
suggested that all conditioned spaces shall follow the G3.1.1.b statement, even if they are not actually cooled.
Could someone please information to clarify this point? Thank you
My understanding is that the intent in Appendix G with this clause is to prevent design teams from gaining an artificial advantage by not modeling a system which is not present in the current design but could be installed in the future, perhaps ignoring the rules of the Standard. But perhaps some exception could be allowed for G3.1.1.b when the design intent and function are clear and justified enough.