FAQs about EAp2 :

Can SHGC be higher in the proposed than in the baseline model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Do I need to justify the electrical and fuel rates I am using in my model?

Our process load is higher than 25%. Do we have to justify that?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

baseline systems

I m modeling a 52 floor building and 2 detached retails buildings,The proposes system are chilled water system with FCU except : 1-8 floors core and shell ( m0re than 78000 sqft) 2- G+2floors retails core and shell (around 20,000 sqft) floors 3-G+1 floors shops core and shell (around 10,000 sqft) as per ASHRAE 90.1-2007 table G.3.1.1.A the basline & proposed systems should be : 1- Packaged VAV DX 2-PSZ-AC 3-PSZ-AC my question is what shall I do if the cooling load of these spaces are considered in the chiller load and tap points are provided in the design? shall i model them as per ASHRAE and deduct the load from the chillers..But that will not be proposed design? what to do?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 06/27/2012 - 09:20

For the C&S spaces you mentioned (1,2&3): Model the baseline as per ashrae (ignore tap points). Model the proposed for these spaces just like the baseline (ignore tap points). Think of it as if the tap points are not used and you have an extra system(s) taking care of the cooling. This is according to the standard. This is irritating because your chiller will be running at a very low part load where the efficiency is rubbish. Any thoughts, Marcus?

Wed, 06/27/2012 - 09:29

Jean, I just noticed that ,As per AHSRAE table G.3.1.1a if I have non-residential more than 5 floors i can use system 8 ( because ihave boilers) but what about the retails? can i say that all part of my non residential? or i have to use system 4? and Jean I am simulating the retails because they are fed from the chillers and boilers if I am going to model them using DX system what is the use of modeling them i can pretend that only my tower is under certification and not these 2 detached retails buildings. What do you think?

Wed, 06/27/2012 - 09:42

Now you're talking about the LEED Project Boundry. Everything in the LEED Project Boundry must be simulated (except non-building shading like trees, or reflective natural features like lakes). As the project boundry effects all credits in the leed rating system, this is not an easy answere. Also, if spaces inside the same building are part of that buildings normal functioning (i.e. needed to funtion, like a parking garage) then it must be included in the leed project boundry. This is according to my current state of knowlege and is my interpretation...in no way sacrasanct.

Wed, 06/27/2012 - 09:49

ok so for the office will use system 4 what about the retails?

Wed, 06/27/2012 - 10:07

Your retail [2- G+2floors retails core and shell (around 20,000 sqft) floors] is (Non-Res) and (3 Floors or less) and (<2300 m² ) system 3 ---PSZ-AC (DX fossil fuel furnace), unless your proposed building boiler is "Electric and Other"

Wed, 06/27/2012 - 13:54

Going back to the original question. Model the Proposed as designed, almost always. The Proposed HVAC system does not really matter, just the heating fuel. Model the whole Baseline according to Table G3.1.1A. Secondary systems in the Baseline can be modeled if any of the exceptions in G3.1.1 apply. So in your case the 52 story building sounds like a system 8 and the two smaller buildings system 3 or 4. To complicate things further since there are three buildings this could probably use the district energy guidance. Jean is correct that the shell spaces should be modeled the same as the Baseline if the systems in those spaces have not been designed according to Table G3.1-10 Proposed.

Wed, 06/27/2012 - 13:57

I forgot to mention that 46 floors are residential so I will use system 2 for them the 8 floors offices I will use system 8 retails I will use system 4. so in the proposed design I will enter the chiller capacity as it it but without taking into consideration the retails because they are modeled as baseline now DX system AM i correct?

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.