I got a review comment as following:
"It appears that the Baseline Case water side equipment (i.e. Chillers, etc.) was selected/sized based on the project LEED CI peak cooling load only, which appears to be inappropriate. Note that the Baseline Case water side equipment (i.e. Chillers, pumps, etc.) type, size and related controls such as COP, Secondary pump control, etc., must be determined based on the whole-building capacity."
In the reference guide, I only see that we should choose baseline HVAC "type" by base building, but concerning of the baseline equipment aotosizing, I think we should simulate by only our project scope? In my case, the base building is 85 floors and my project only occupies half floor. When I autosize baseline equipment by whole building, the equipement capacity is so large that the loading of chiller is so small, which is not reasonable.

Is there anyone with the same problem? Thanks!!