FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

Baseline System Fan Power...

...is calculated automatically by the energy simulation tool we use according to appendix G13.1.2.9. However, we would like to check the outputs of the model against equation in G3.1.2.9 to verify that the fans are modeled appropriately. Equation G3.1.2.9 for systems 3 through 8 indicates that the Fan Power equals to 746/Fan Motor Efficiency in Watts. Fan Motor Efficiency is "the efficiency from Table 10.8 for the next motor size greater than the input kW using the enclosed motor at 1800 rpm". What is it meant by "...input kW"? Do I check the size of my motor in Proposed and then choose the next greater corresponding one in Table 10.8, and use its efficiency (under enclosed motors at 1800 rpm) by dividing it with 746?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/23/2013 - 13:29

It has nothing to do with the proposed motors. The input kW is the electrical power into the motor as opposed to the output kW which is how much work (energy) the shaft produces. The difference is the efficiency. Input is typically derived and the motor nameplate provides the output. The size of the baseline motors is determined by the supply cfm auto-sized by the baseline energy model. See Table G3.1.2.9. There is a spreadsheet under the Documentation Toolkit button above that does these calculations which you can use to check your modeling results.