CS-v4.1 EAp2:Minimum Energy Performance

Baseline System for a data center

I am working on a Data Center project which is located in Zone 4A. the project is assessed based on C&S. I am confused about the baseline building system selection.

As expected the is predominantly a data center (computer room based on ASHRAE 90.1 definition) there are some office areas and support facilities with significantly lower loads. Am I interpreting the ASHRAE guideline correctly to not include exception “c” and “g” and determine the system based on total conditioned areas.

If the first assumption is correct based on total conditioned area, system 7 should be chosen. Then I wonder if I could exclude economizer from the baseline building as based on section G3.1.2.6.1, economizers should only be applied to System 11.

System 11.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 06/08/2021 - 13:52

Sorry, can anyone help me and give me some advice on above enquiries?

Tue, 06/08/2021 - 15:29

Since the predominate building type is a computer room it appears to me that exception g applies so that part of the building is a system 11. It is then likely that exception c applies to the office/support areas. 