Hi to all,
Our project scope is modeling one floor of a 20 stories office building. It is clear that we must use system 8 for the baseline based on the full office building geometry.
The question is: should we model the complete building and then prorate the energy use only for our scope portion, or should we model just only the floor that is part of the leed project?
Id appreciate so much your support.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
April 16, 2018 - 10:55 am
The Reference Guide outlines two methods you can use to account for systems that are outside the project's scope of work.
Depending on the systems in the building you may need to model more than the floor, but the methods described allow you to allocate the HVAC loads to your single floor. So most projects only have to model the scope of work for the LEED project.
Paula Hernandez
MRS.PAH&A
85 thumbs up
September 10, 2019 - 2:11 pm
Hi,
Taking this question, I would like to verify the following:
- In may case, the whole building has the same schedule, so I am using the Adjustment Factor method.
- I only have to model the Floor in the LEED scope of work.
- The main building HVAC system consists on water and air cooled chillers, corresponding pumps and cooling tower.
- Adjustment Factor = Scope of Work surface/Total Surface Served by the chilling water system.
- For each equipment in the HVAC main system I apply:
Is this right?,
Thank you!
Tyler Thumma
7GroupLEEDuser Expert
67 thumbs up
October 3, 2019 - 1:36 pm
That is correct, and would be done for all parameters relevant to the chilled water system (chilled water flow rate, condenser fan power, etc.).
Paula Hernandez
MRS.PAH&A
85 thumbs up
October 3, 2019 - 2:03 pm
Thank you Tyler!
Omar Elrawy
Green Building Consultant | ResearcherGreenA Consultants
56 thumbs up
June 4, 2020 - 8:25 am
relevant to this,
I have a case in which my space and other spaces are served by one AHU, so I considered that my AHU air flow (lps) = Adjustment Factor x whole floor's AHU flow (lps).
But if I do the same for the AHU fan power I'm getting to model (virtually) a fan that is not efficient at all (less than 20% efficiency), and not getting any savings, so in such case, I intend to keep the AHU fan efficiency constant, adjust flow rate, and keep fan power automatically calculated based on actual fan efficiency, is this acceptable?
Tyler Thumma
7GroupLEEDuser Expert
67 thumbs up
June 10, 2020 - 3:08 pm
This does not appear to be acceptable, as it will not result in a proportionate amount of fan power for the AHU being applied to your space.