FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Baseline System 8

Greetings, Just a small clarification about the heating plant of System 8. It is written that heating is Electric resistance. For VAV w/PRP Boxes, the reheat is electric resistance - OK. Should the same approach be applied for the heating coil of the Main AHU or there should be Electric resistant boiler? If however the boier is the case, how are the hot water temperatures be determined. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 03/22/2016 - 15:19

Electric heat is only in the boxes. The only exception is if the proposed has some sort of preheat, then electric heat goes there as well. No heating coils in the AHU and no electric boiler.

Tue, 03/22/2016 - 15:53

Thanks for the reply. Something however is still kind of unclear. The proposed heating plant is electric boiler supplying hot water to the systems' heating coils. The Baseline systems have heating coils assigned to: - Main AHU - VAV reheat boxes How come that the Main AHU remains without heating coil? Could you please explain as I'm sort of puzzled. Thanks

Tue, 03/22/2016 - 16:15

The preheat is covered by G3.1.2.3. The fact that you will only need heat in the boxes is based on the baseline having to comply with G3.1.2.8 and G3.1.3.12. You typically do not need extra heat in the air handler in order to comply. If you do I suppose you could add it but in our experience you never need it.

Tue, 03/22/2016 - 16:32

Tanks for the reply. Probably there is kind of interpreting misunderstanding - from my side. It appears that what you call "preheat" is the heating coil which is in the AHU serving the VAV boxes of the system. As this is zone 5A there is always such preheating of the OA before entering in the VAV boxes. Hope that now I've understand it properly, or ? Thanks

Tue, 03/22/2016 - 16:56

It can be in the AHU or it could be in a separate DOAS system. You only have it in the baseline system if it is in the corresponding proposed system.

Add new comment