FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Baseline PTAC sizing

I have a residential facility seeking LEED v2009 certification with small room loads (approx 2,000 BTU/hr). My understanding of ASHRAE 90.1-2007 is that these spaces need to be modeled with PTACs oversized by 15% (2,300 BTU/ hr). The PTACs scheduled are much larger (approx 8,000 BTU/hr) than the load as a small enough PTAC in this particular line is not available. I've heard a rumor that there is guidance that makes it permissible to model the baseline units with a capacity larger than the 15% oversized specification if such a unit is unavailable. So in this case, an 8,000 BTU/hr unit can be used instead of a 2,300 BTU/hr unit in the baseline. I'm trying to put an end to this rumor with a label as fact or fiction. Can someone help me?

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 03/27/2012 - 17:11

Fiction. The only allowance for going over the 15% is outlined in G3.1.2.2 and is related to reducing the unmet load hours in the Baseline if you are over the limits. The Baseline model's HVAC system design does not need to get designed or installed. It simply gets modeled according to Appendix G. So the availability of PTACs in a certain size range is not applicable to the situation.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.