FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

A portion of our building envelope is historic. Can we exclude it from our model?

Our project has a diesel backup generator. Should we include it in our energy model?

For an existing building, do I need to rotate the model?

Can SHGC be higher in the proposed than in the baseline model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Do I need to justify the electrical and fuel rates I am using in my model?

Our process load is higher than 25%. Do we have to justify that?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Baseline for Interior glass

What should be the baseline for interior glazing such as for atrium and partitions? Generally, the designed case will be SGU with high U value and SHGC.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 11/27/2014 - 14:17

Most interior windows are not regulated, i.e. has the same as the proposed design...the exception is semi-heated spaces...those can be found in the usual tables with pointers to App. C for some types.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.