FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Baseline HVAC system choice

Let's Say this building is 26,000 sf which the baseline is system 5-6. What if the exception area is 10,000 sf (process load difference >10 Btu/h ft). This will make the rest of building area to be 14,000 sf. Thus, this 14,000 sf needs to be use system 3-4 intead (since it is less than 25000 sf). In this case, the system 5-6 is no longer become this building baseline. Am I correct?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 05/26/2015 - 13:54

You got it (except your math is off 2000 sf). :-) I personally do not agree with this interpretation but that is how USGBC applies it to LEED projects.

Tue, 05/26/2015 - 14:03

Sorry for bad math In my case, reviewer specificly mentioned that my base building is system 5-6 but they ask me separate the exception zone out. This make the area for system 5-6 left only 23500 sf. Can we maintain system 5 or 6 for the majority of the building? We are afraid that if we change model too much it will raise other issue. Not all GBCI reviewers are well aware of all CIR. Also, System 5-6 will give the baseline the better result than system 3-4 anyway. Changing from 5-6 to 3-4 requires too much painful work.

Tue, 05/26/2015 - 14:34

If the reviewer did not ask you to change the baseline system or suggest that you reevaluate it, then you should be able to get away without having to change it. If they asked you to look at the baseline system selection you should change it.

Tue, 05/26/2015 - 14:42

I have a similar situation where there is a 77,000 ft2 school building, within which there is a 40,000 gym that has 20 btu/hr-ft2 load difference from the rest. Should I apply system 3 on this or system 5? Could you let me know where is the CIR that specify how we treat this? Thanks

Tue, 05/26/2015 - 15:02

If the gym qualifies for exception b to G3.1.1 you must apply it. The exceptions to G3.1.1 are required. The gym sounds like it should be a system 3 and the remainder (37000 sf) a system 5. I am not aware of any LEED Interpretations that state this policy of subtracting the area when applying an exception. It may make some sense for exception a but i personally do not agree with it in general. If you look at the Advanced Energy Modeling Guide for LEED it can be interpreted as contradicting this review policy. Unfortunately this is one of those hidden policies that I do not think have been made public. For the vast majority of projects this is not an issue.