FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Baseline HVAC system with 2 predominant spaces

Dear All,

We have a projects designed for commercial purpose with 3 main spaces types:
- Restaurant: ~34,000 s.ft., 10 stories
- Offices: ~40,000 s.ft., 9 stories
- Retail: ~12,000 s.ft., 2 stories

The whole building consist of more than 5 floors and does not provide heating in the proposed design, therefore it is determined that System 8 shall be adopted as the baseline HVAC system. According to the building peak cooling load (>300 ton), 2 water cooled chillers with equal size shall be provided in baseline model.

However, we found that the peak thermal load of those 3 spaces differ by more than 31.2 W/m2 from each of them, i.e. Restaurant: ~350 W/m2, Retail: ~215 W/m2, and Office: ~175 W/m2.

In such a case, I should set Office spaces as System 8 (due to its area), then set Restaurant and Retail as System 4?

If so, I should determine the water side again by the peak thermal load of Office spaces ? i.e. If the load of Office spaces is below 300 ton, only 1 water-cooled chiller shall be provided?

Grateful if someone could confirm by interpretation. Thanks a lot!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/02/2018 - 14:07

Your general approach sounds right. Basically you are required to apply the exceptions to G3.1.1. If any of those exceptions apply then you subtract the area and reenter Table G3.1.1A. Sounds like an odd building with 10 stories of restaurant. 

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.