Forum discussion

CS-2009 EAc1:Optimize energy performance

Baseline HVAC System

We are using packaged VAV with reheat system 5 for the Baseline System. In sizing the baseline heating coils and fans within this system should the air flow rates and and on coil / off coil temperatures match the proposed building system.?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 04/25/2016 - 14:39

The airflow rates are auto-sized along with the heating capacity. See G3.1.2.2 for equipment capacities, G3.1.2.8 for airflow rate/temperatures, and G3.1.2.9 for fans. The room temperature settings should be identical to the proposed.

Sun, 05/08/2016 - 20:31

Thanks Marcus. Just wondering should the Outside Air supply rate be the same for the proposed and baseline rooms modeled ?

Mon, 05/09/2016 - 13:25

Unless the proposed has demand controlled ventilation the total outside air should be in the same in both models. Since you do not necessarily create a model on a room-by-room basis I am not sure it translates down to the room level. A system #5 according to G3.1.1 must be modeled as a system per floor. So the OA for that system on that floor should correspond to the total outside air of the proposed systems serving that floor.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.