FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Baseline heating set-point when no heating system exists

According to ASHRAE 90.1 (2007) Table G3.1 - 10 c, "where no heating systems exist, HVAC system shall be assumed to be electric". Considering a space that has a cooling system but not a heating system, can you please clarify: 1) which shall be the "virtual" heating set-point for these spaces? 2) in the particular situation of a factory where the space temperature is allowed to fluctuate down to 10ºC, can the "virtual" heating system be adjusted (because good thermal comfort levels are not expected)?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 04/17/2015 - 13:45

Adding systems that do not exist in the design is required for both heating and cooling. The easy work around is to set the temperature in the space so that the system never comes on. As long as you have the same temperature in both models this is allowed. So adding a system that does not exist is just a waste of time. What I do is tell the reviewer that I am aware of this work around and therefore did not go to the effort required to model the system. The end result is the same so the reviewer should accept it.