FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Baseline Garage Ventilation

Greetings, In our project (registered as per LEEDv2009) there are several garage ventilations. According to ASHRAE 62.1-2007, the garage exhaust rate is to be sized to 0.75 cfm/ sq.ft. In the Proposed model, the rate of the actual project however is sized to the local norms which is less than those of the standard. Additionally there is a CO control sensors, which setting is on a CO concentration of 20 mg/m3. From other site, the minimum air flow of the Proposed is always greater than 0.05 cfm/ sq.ft. as per the requirement of CIR 10371. The question is: Are there any circumstances that prevent entering the garage rate in the Baseline as per the standard and at the same time to enter the garage ventilation rate in the Proposed as per the actual design. You support is highly appreciated. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 06/26/2017 - 14:03

Sounds like you got it. Just follow the guidance in the interpretation when claiming savings for DCV in a parking garage.

Mon, 06/26/2017 - 17:41

Hi Marcus, Thanks for the reply. Just one more question to this issue. How to calculate the fan power for the Baseline Garage exhaust. The air flow rate is clear, but the fan power? Probably it should be like for System 9/10 - CFM x 0.3. Thanks

Mon, 06/26/2017 - 18:43

Baseline system fan power shall be calculated at 0.3 watts per CFM.