Baseline Fan power

I’m modeling a typical office building which operates 5 days/40 hours per week. In order to comply with G.3.1.2.4, I broken out the fan power from system EER. it’s mandatory to cycle the fan during unoccupied hours (night/weekends)? I’m not clear with G.3.1.2.4 interpretation. Any help appreciated.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 04/10/2013 - 14:43

For certain systems the fan power needs to be broken out from the efficiency. This typically applies to units where the fan cycles with the call for heating/cooling. See G3.1.2.1. Some software does this automatically and some does not. There is an example in the User's Manual. It is mandatory to cycle the fans during unoccupied hours.