FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Baseline Envelope NonResi/Resi U-Values

Our project is a multi-family residential project (8 stories) and we have modeled the baseline roof as a Residential, Insulation Above Deck U-Value per Table 5.5-1. We have received a LEED Review Comment back stating that "Note that the residential area must comprise 60% or more of the space usage for this building in order for it to be classified as a residential facility. If the project cannot be classified as a residential facility based on the definition provided, revise the roof constructions in the Baseline model " We have seen several opinions posted on LEED User in how to model Non/Resi Envelopes: (1) To model all residential floors with Residential U-Values and to model all non-residential floors with non-residential u values (2)To model all residential zones with Residential U-Values and to model all non-residential zones with non-residential u values I have never seen this reference of 60% when discussing the classification of Non-resi/Resi U-Values. (I have combed through Addendum and CIRs). We have 59% of floor area devoted to the apartment units. The remaining area is corridors/ MER/ storage, amenities and based on the LEED Review comment would need to update our Baseline Roof to non-Residential. Does anyone know if there is specific language in Appendix G or USGBC documentation which states how Non-Resi or Resi is determined?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.