FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Baseline EER - System 2 PTHP

As per Table 6.8.1D, I observed the following EER = 12.3-(0.213*Cap/1000) EER Also, Cap means the rated cooling capacity of the product in Btu/hr. If the unit's capacity is less than 7000 Btu/hr, use 7000 Btu/hr in the calculation. If the unit's capacity is higher than 15000 Btu/hr, use 15000 Btu/hr in the calculation. Questions: What capacity used in the calculation for capacities between 7000 Btu/hr and 15000 Btu/hr. (This is not mentioned) Capacity should be arrived from basecase energy model or proposed havc system's capacity If arrived from basecase means, whether the coooling, heating capacity should be oversized by 15%, 25% respectively or not? What is the meaning of rated cooling capacity of the product? (is this based on proposed model of ac system) Please help.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sun, 04/16/2017 - 05:58

could any one help me on the query above? Please

Fri, 04/21/2017 - 14:41

We have a saying - good, fast, cheap - pick two. I won't compromise good and I do this for free so . . . sorry for the delay. The table serves dual purposes. For the baseline system efficiency determination - Between the minimum and the maximum capacities (7,000 and 15,000) you use the actual capacity derived from the auto-sizing in the baseline model based on the 15%/25% oversizing requirement. This table in the standard is also used to spell out the minimum efficiency required of the proposed equipment. This is a mandatory provision so the proposed equipment must comply. In that case you would use the rated or actual capacity of the equipment.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.