Can ASHRAE 90.1 - 2010 Table 6.5.1B be applied to a LEED PRM models. For example we have an IT / computer server room where the load is less than 40kW - therefore am I correct in saying that an economiser is not required for the Baseline System 3 system in this instance given the small load. Our Climate Zone is 5A.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5921 thumbs up
September 5, 2019 - 12:41 pm
Yes I belief that is correct.