NC-2009 EAc1:Optimize energy performance

Baseline during unoccupied hours

In an EAp2 appeal we were denied a 87 % cooling energy saving. The reviewer consider it unlighty to have cooling demand during winter during unoccupied hours. However, the Baseline system shall have a supply air temperature of 15.3 degrees C and the return air temperature from the zones are about 20 degrees C. So obviously there is a cooling demand. As baseline has high U values in comparisson with Proposed (heated with radiators, nor air) the cooling savings becomes great. How should I address USGBC about this issue? I have some more building like this coming up and need general arguments. And also, why does the temperature have to be 15.3 degrees during unoccupied hours? Why just not recycle it directly back at an higher temperature (if you have a heating demand)?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 09/20/2013 - 13:42

I am not aware of any specific requirements for unoccupied temperature settings within Appendix G. The baseline supply airflow is based on a delta T between supply air temperature and occupied space temperature. Unoccupied space temperature setting are typically the same or higher than the occupied setting so the delta is easily maintained. Perhaps I am not understanding your issue?

Fri, 09/20/2013 - 14:00

Thank you Marcus. It is probably me who have missunderstood the supply air temperature settings and HVAC systems for baseline. We never use recyceled air in our Project systems so I don´t have experiance of these systems. So can you tell me; In Baseline, during unoccupied hours, during heating demand, are any return air beeing cooled before reentering the zones? Or is it as I see most natural, that one just recycle the return air back to the zones and then heat it in the reheat coils

Fri, 09/20/2013 - 16:23

What is your baseline system type?

Mon, 09/23/2013 - 05:26

It´s System 7 - VAV with reheat

Mon, 09/23/2013 - 14:57

For a system 7 during unoccupied the outside air is shut down so all of the air is return air. If any of the zones call for cooling during unoccupied (which depends on the unoccupied temperature setting) then the air would be cooled.

Add new comment