FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Baseline for curtain wall

A curtain wall is made of glazed parts and opaque parts (spandrels). In the baseline model, how much shall the façade be glazed? Are spandrels considered as an opaque wall or as a frame?

Does the U-value of Table 5.5- Metal framing (curtainwall/storefront) include both the transparent parts and the opaque parts?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 07/06/2018 - 15:34

Opaque spandrel panels within a curtain wall system are considered wall area.

Mon, 10/21/2019 - 14:35

Marcus,   Am following up on Francessco's question here... Does the U-value of Table 5.5- Metal framing (curtainwall/storefront) include both the transparent parts and the opaque parts?  I've read that with mullions and spandrels the R-12 value  is the most most efficiency you can get... how does this relate to this table Table 5.5- Metal framing as well?

Mon, 10/21/2019 - 19:26

For a spandrel, you're compared to the opaque wall, because the definition of "fenestration" in Section 3.2 is an area that "lets in light", and spandrels don't. So for example, in climate zone 4A, the glazed panels + frame are compared against U-0.50; whereas the spandrel panels + frame on the same curtainwall system will be compared to the much more stringent U-0.064. That's the figure in Table 5.5 that you need to use for the model for spandrel panels areas.  So, you can say that overindulging in spandrel panels in pursuit of a certain architectural aesthetic will penalize the project energy wise. You can recommend adding insulation behind the spandrel, but you'll need to account for the thermal bridging of the frame too. Kawneer has charts for some of their systems when tested according to AAMA 507 for various levels of spnandrel insulation. 

Wed, 10/23/2019 - 18:09

Waleed,   Thank you, I understand better how to deduce U-Factor of U-0.064 (Steel-Framed Above Grade Wall) under Climate Zone 4 for the spandrel area considered/treated as a wall area because it does not let in light within a curtain wall VS. the Curtain Wall area with Glazing within the same Climate Zone would be U-0.50 for the Base Building. But am assuming that curtain wall should have an overall area weighted average U-Factor of both the spandrell and glazing combined (U-0.50 and  U-0.064) which will be inputted into the baseline building model, is this correct?     Just a side note: we are using YKK AP America Inc's  curtain wall unit which apparently calculates thermal performance per AAMA 507. I will see if the product data sheet shows that the testing accounted for various levels of spandrel insulation But for the Proposed Building, because we do not have NFRC labeled fenestration, I am using the values under the  Unlabelled Fenestration Table 8A.2 under Frame Tpe "Metal and other frame types Double Glazing" U-0.90 for both Tinted and Clear Glass? Does this approach make sense?   Just read this from the user manual "When a building has more than one class of construction that falls within the same space-conditioning categories, area-weighted averaging can be performed using the U-factor, C-factor, or F-factor, compliance option. Area-weighted averaging is not allowed for R-value compliance. Area-weighted averaging enables one construction assembly within the class to fail to meet the criteria as long as other constructions within the class exceed the requirement. However, the area-weighted average of all constructions within the class must be less than the U-factor, C-factor, or F-factor criteria.  When doing area-weighted averaging, up to one percent of openings due to recessed equipment can be ignored. If the openings are greater than one percent, they need to be accounted for in the area-weighted average."

Thu, 10/24/2019 - 14:31

I think what you input in the model is a combination of what the tool allows you to do and being a judgment call. If I were to model it, I'd model spandrels as an actual wall not a curtain wall, and only model the vision glazing as a curtain wall if that makes sense. That way I can troubleshoot easier. That also makes sense because a wall doesn't take a SHGC value and a glazing does. If you're modeling daylight dimming that's a third thing to average. So I just avoid that and model them separately as opaque wall and transparent glazing, where spanrels will be categorized as opaque wall. U-factor averaging is certainly acceptable in many scenarios, and that's essentially what we do when accounting for thermal bridging.  That excerpt from user manual seems to refer to class of construction though, as in above/below grade walls, or mass wall with some steel stud portions, etc. 

Thu, 10/24/2019 - 14:33

As for the proposed U-factor, I recall LEED might allow you to model the glazing using WINDOW if you don't have an NFRC label? I'm not sure. But a baseline of U-0.5 against a proposed case of U-0.9 seems like a steep penalty.