Per 90.1-2007 section 6.4.3.9 "Ventilation Controls for High-Occupancy Areas" systems are required to have DCV given certain criteria. Appendix G seems to not mention anything about ever requiring demand control ventilation, but I always assumed the baseline building had to meet all code requirements elsewhere in 90.1 unless otherwise noted in Appendix G.

If a baseline system meets the criteria to require demand control ventilation per section 6.4.3.9, is it required to be modeled that way? Are there any other similar items dictated by 90.1 that aren't required for the baseline building since Appendix G doesn't mention them or is it as simple as: "it's required unless Appendix G says otherwise"?

Additionally I have the case where one of my systems that may require demand control ventilation on its own is being grouped into a single VAV system per Appendix G. But the rest of the thermal blocks in the VAV system don't require Demand Control Ventilation so how do I account for that?