Greetings,
ASHRAE 62.1-2007 establishes a ventilation exhaust rate for garages of 0.7 cfm/sq.ft.
Our project has lower rate and besides it applies a CO control settings of 20mg/m3.
The question is:
Is it OK if in the Baseline we enter the rate as per the standard and in the Proposed - the actual design rates.
Thanks