FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Base HVAC System for a Data Center / Server Room ASHRAE 90.1 - 2007

  • Modeling a Data Center: 1,682.34 sq. ft.
  • Call Center: 8,389 sq. ft.
  • Offices: 4,600 sq ft.
  • Common Spaces/Other: 17,126

The data center has an IP load with a power density of 3.2 kW/m2 or 297 W/ft2. The room has a separate HVAC system in the baseline building. The question is - does it mean that system 13 should be applied for the Baseline. The proposed HVAC is not designed with VAV. It is Liebert units with glycol dry coolers with free cooling.

However the Dry Cooler loop also serves two other rooms: UPS Room and a Call Center (for supplemental cooling for a large Media Center. The call center already has a two roof top units that heats/cools the space). Offices and other common areas have thier dedicated systems as well in the proposed design.

First question is - Is System 4 appropriated as the baseline HVAC?

Second, looks like I may need to also complete this calculator "2009 and v4_Minimum Energy Performance Data Center Calculator_v02.1"  in addition to the Energy Model and the "v2009_Minimum Energy Performance Calculator_v09". Is this correct?

Thanks in advance for your help!

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 09/12/2019 - 17:17

1. Based on the floor areas you listed, the primary Baseline HVAC system serving the non-data-center spaces would likely be System 5 or 6 depending on the heating source, assuming that the total conditioned floor area of the non-data-center spaces is greater than 25,000 square foot. The data center itself would qualify for G3.1.1 exception b, so would be modeled with System 3 or 4.  2. The Data Center Calculator is helpful but not required unless you are modeling savings for the data center equipment as an exceptional calculation.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.