EBOM-2009 EAc3.1:Performance measurement - building automation system

BAS - whole building

If our project's BAS controls 100% of the building's heating and air conditioning, but only 35% of the building's ventilation (by square footage), can we still pursue this credit? (Lighting is automated under a separate system.)

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/11/2014 - 20:28

Hi Melissa - It sounds like your project would not qualify, unfortunately. From my understanding, 100% of building HVAC systems would need to be covered.