BAS Report as Functional Testing

Is it acceptable to use the BAS test results as a form of functional testing?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 01/29/2020 - 14:45

Hi Shannon, You haven't explained the content of your BAS test. I think the reviewers will look for most of the following verifications: measurement validation, energy and water usage profiles, reporting capability, storage capacity, alarms, access privileges...

Fri, 02/28/2020 - 20:29

Short answer is...no. Just testing the sensors and actuators of a BAS system is only the very first part of functional testing. The real value of the testing is sequences...confirming the correct response/action of the system to match the Sequence of Control.