I am working with shopping mall project. each shop has equipped with FCU units for air conditioning while separate treated fresh air AHU (PAHU) is supplying fresh air to each shop. Is there any method to assign a single shop to both FCU and PAHU in eQuest? Consider both FCU and PAHU are connected to same chilled water system.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5921 thumbs up
June 8, 2018 - 12:51 pm
There are two ways to do this. You can set up a dummy zone or you can assign the PAHU proportionally to each FCU (both the cfm and fan power). There is extensive discussion on this subject within the eQUEST Users group you can find at onebuilding.org.