FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

ASHRAE 90.1 - Section 8 Voltage Drop

In the section 8.4 Feeder conductors shall be sized for a maximum voltage drop of 2% at design loadand branch circuit condutors shall be sized for a maximum voltage drop of 3% at design load. I'm working in a project that has 3 substation which feeds the block 3 that will not be certified by LEED, from the QGBT-SE3 (CIRCUIT BREAKER or LOW VOLTAGE DISTRIBUTION BOARD ) of this substation runs a extension, which feeds a QGBT PREDIO ADM (CIRCUIT BREAKER), about 80 meters away from the QGBT-S3, this QGBT PREDIO ADM feeds the lighting and the power of the ADM bulding,which will be certified. Questions. - Because only the ADM building will be certified, the maximum voltage drop should only be considered in the building or from the substation? - As the voltage drop between the circuit breaker (QGBT PREDIO ADM)and the lighting points to be fed is very small, the calculation of voltage drop could be done in reverse, 1% for the circuit breaker to the outlet or load and 3% for QGBT-SE3 ?

4

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 06/29/2011 - 15:18

If only the ADM building is being certified, the requirement only applies to the systems inside the building.