CI-2009 EAp2:Minimum energy performance

ASHRAE 90.1 mandatory provisions

We were asked to make a preassessment of a project which wants to get LEED CI certification. The tenant's scope of work includes only small alterations of the space like moving some of the internal walls and bringing their own furniture and office equipment. HVAC systems, lighting, water fixtures and external walls won't be changed. I'm not sure if in this case the project can comply with the requirements of EA Prereq2. It seems that none of ASHRAE mandatory provisions fall within the scope of tenant's work. Does it mean that this project is exempt from ASHRAE 90.1-2007 requirements (EA Prereq 2 requirements) or that the project is not eligible for LEED CI certification?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/14/2012 - 15:49

You only need to meet the 90.1 mandatory and prescriptive requirements that are part of the scope of work. So if none apply then you do not need to make changes. I think this applies to the 10% lighting power reduction if the lights are not in the scope. Any new equipment needs to comply with the Energy Star requirement.

Thu, 08/16/2012 - 13:04

Thank you for your reply! I just wanted to clarify two things: 1. So if the tenant is not changing the installed lighting then he doesn't have to comply with the 10% reduction requirement? And if the tenant brings additional task lighting (not permanently installed desk lamps connected to the plugs) then does he need to meet the above mentioned requirement? Should this kind of task lighting be included in the interior lighting power allowance calculations. In the reference guide I read that calculations should include only permanently installed lighting but after reading some of the comments here I got confused. 2. You wrote that any new equipment needs to comply with the energy star requirement. So if the tenant is taking only his old office equipment from the previous location then he doesn't have to comply with this requirement? And if he buys only a few new computers then should he include only these new computers in the calculations and exclude the old ones?

Thu, 08/16/2012 - 16:20

1. The addition of task lights complicates the issue. Task lights are typically required to be included in the calculation of lighting power density. Where specifically in the Reference Guide does it state that only permanently installed light fixtures are included and task lights are excluded? EAc1.1 lists task lights as part of the calculation. Since they are not temporary lighting and will be installed as part of the scope of work I think they must be included. 2. After reviewing the Reference Guide and credit interpretations for EAp2 and EAc1.4 it appears that all of the equipment that is rated by Energy Star must comply and is not exempt from this prerequisite requirement. EAp2 refers to EAc1.4. The Reference Guide clearly states that all installed equipment and appliances that are eligible for Energy Star apply. LEED Interpretation #2090 confirms this approach. For old equipment it must comply with the Energy Star criteria in effect at the time of purchase. For new equipment it must comply with the current criteria.

Fri, 08/17/2012 - 09:49

Aha, regarding the lights - I missunderstood it then, thank you for clarification. So if the tenant brings only additional task lights he has to comply with the 10% reduction requirement but does he also have to meet the requirements of sections 9.4 and 9.5 of ASHRAE standard which are not associated with the task lights? If the tenat decides not to add any lighting he is exempt from all above mentioned requirements, right?

Fri, 08/17/2012 - 13:06

I think that would be correct since only the task lights are in the tenant's scope of work. CI projects only need to comply with requirements in alignment with the tenant's scope of work so yes if the lighting is already installed and the tenant is not installing any new lighting it does not have to comply.

Wed, 08/29/2012 - 12:19

Marcus, you wrote that all equipment (existing or new) should be included in the Energy Star calculations however I was reading the addenda for LEED Reference Guide for Green Interior Design and Construction 2009 and on page 17 it's written: "Only new appliances and equipment purchased as part of the scope of work for the project need to be included in the credit for EA Prerequisite 2 and EA Credit 1.4". Moreover I was reading a discussion regarding this subject here on LEEDuser (July 2010, page 4) and it seems that they confirmed that only newly purchased equipment should have Energy Star rating. Can you clarify this? Maybe something changed since the publication of the above mentioned addenda?

Wed, 08/29/2012 - 13:22

Adam, You are correct, only new equipment must be included. If the project is reusing existing equipment, it does not have to be included as part of the calculation.

Wed, 08/29/2012 - 14:05

Missed the addenda in my search Adam and if Amy says it is so, it is so. Personally I think this addenda change is ridiculous. A project is now incentivized to keep inefficient equipment and all they have to do is buy one new Energy Star item to qualify. Office equipment is one area that the tenant has had continual control over unlike the lighting and HVAC in the newly leased space. Unfortunately too many LEED "rules" loose sight of the credit intent in the name of easier credit attainment. The intent here is to save energy and the original method (including all appliance and equipment) properly incentivized at least marginally good practice in this area. For most projects this just adds another easy credit to a system now over-run with easy credits which have marginal effect.

Thu, 10/04/2012 - 05:53

The problem with focusing solely on energy efficiency is that wider environmental impacts are missed. It is not simply a matter of buying new Energy star compliant equipment. Where a tenant uses perfectly viable existing equipment it avoids the impacts of manufacturing new equipment and the impacts of disposing of electrical/electronic waste. In addition, I doubt if any tenant's IT team would want to have to reinstall software and files on new machines, so my vote is for the 'easy' but logical credit!compliance

Thu, 10/04/2012 - 14:27

John I think you are not correctly interpreting what I am saying. I am not suggesting that anyone dump viable IT equipment and replace it with new. The tenant has had constant control over these purchase decisions since before they moved into a new space. If the company had any sort of broader environmental focus then the used equipment would already be Energy Star compliant at the time it was purchased. I am suggesting that all of the equipment new and used be included in the evaluation of credit compliance. We did a CI project a couple of years ago. They did not buy any new equipment but the vast majority of the existing equipment was already Energy Star qualified at the time of purchase. We did a very easy inventory and demonstrated credit compliance without buying any new equipment. Doesn't get any easier than that. So I am not saying that they should dump perfectly good equipment and buy new. That would be antithetical to common sense and the environment for the reasons you point out. I am saying that if they don't already use or buy new Energy Star equipment then they should not be able to earn this credit. The problem with "easy" in LEED is that it typically means there is minimal effect. The purpose of LEED is the create effect in the market so too many gimme credits in the system results in a plaque for the status quo and not anything I would label with a leadership standard. As it now stands LEED is so easy overall that about half the projects are Gold certified. The market has caught up so as we make the current version of LEED easier it frankly looses some of its meaning. The current credit compliance is logical if all we care about is getting a point in LEED; it is illogical if you truly care about minimizing the overall environmental impact of IT equipment and using LEED as a means to that end.

Tue, 10/30/2012 - 21:11

I have a follow-up question concerning the lighting. We have a CI space in which most of the lighting was provided by the base building and not altered in the scope of work. We have a few pendant lights that were added and some task lights in the open office areas. Am I correct in assuming that the only lights that need to demonstrate compliance are the new pendant lights and the task lights? It seems like having only that wattage represented for the entire square footage of the office would not be an accurate reflection of the LPD reduction. Thoughts?

Thu, 11/15/2012 - 21:10

I just wanted to follow up on the question I asked on October 30 - I posed the same question to GBCI and received the following response. I thought I would share..... Thank you for your inquiry, regarding EAp2. For EA prerequisites, all systems installed as part of the LEED-CI project scope of work must comply with the requirements of each of the applicable prerequisites. In addition, all lighting, whether or not installed as part of the LEED-CI project scope of work, must be included in the lighting power calculations in EAp2 to determine the lighting power reduction. Points are available in the EAc1.1 suite of credits for efficiency improvements above the minimum requirements of the prerequisites. All lighting is required to be included in for EAc1.1 and EAc1.2.

Thu, 02/14/2013 - 09:48

We encounter projects where the tenant occupies a building in which the landlord installs general lighting as part of the base building scope, but the LPD far exceeds ASHRAE requirements, suggesting an expensive redesign of the (sometimes new) lighting system, which appears wasteful! In seeking a workaround reference to the ASHRAE 90.1 User Manual is encouraging "The lighting power density requirements of the Standard apply to new lighting systems in any space in an existing building. A new lighting system is one that replaces 50% or more of the existing luminaires in any building space. A renovation of a space that replaces less than 50% of the existing luminaires in that space is not required to comply with the Standard, unless the renovation increases installed lighting power." It seems that the Checklist (above) reinforces this with "In a remodeling project, if new lighting is replacing less than 50% of the total installed wattage, the project is exempt from reducing LPD 10% from the ASHRAE 90.1-2007 standard. However, you still must comply with all mandatory requirements for controls and wiring.". However, compliance with ASHRAE 90.1 may not mean compliance with EAp2? In the Implementation section of the Reference Guide it states "If provisions of the base building are managed entirely by the landlord (and therefore cannot be changed by the building tenant) and do not meet the requirements of AHRAE 90.1-2007, then only areas that are not part of the tenant scope of work and exclusively controlled by the landlord are exempt from the requirements of the standard." Maybe this explains the GBCI's response to Ellen's query? Thus, when the tenant takes over the lighting system and the landlord has no further control, the tenant must redesign the lighting in the tenant area to comply with ASHRAE 90.1!