We're working on a TI office project of less than 5,000 sf in a building that is larger than 5,000 sf. I had a question about ASHRAE 90.1 2007 sections 9.4.1.1 and 9.4.1.2 about automatic lighting shutoff and space control.
As a TI space in the scenario described above, do we need to comply with 9.4.1.1 given our
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
July 16, 2014 - 2:46 pm
9.4.1.1 - Applies to the building as a whole, not just your space.
9.4.2.1 - Yes manual switching is an option in most spaces. Automatic controls are required in the spaces listed under "a".