FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

ASHRAE 90.1-2007 - Section 8.4 - Voltage drop

We are working on the LEED certification for a hospital building with 10 floors height. In ASHRAE Standard 90.1-2007 Section 8.4 the voltage drop limits are 2% for feeders and 3% for branch circuits. In normal conditions the normal network transformers are feeding the loads and the voltage drop limits are met, while in up-normal conditions local generators are feeding the loads through a long feeder (100 meters) and the voltage drop in this case will be difficult to be met. Our question is: do we have to meet the voltage drop limits for the up-normal (emergency) conditions as well as the normal conditions? Noting that in order to meet the LEED requirements we need to double the feeder size and accordingly double the cost. Also note that the overall 5% voltage drop are met in the normal and up-normal conditions.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 09/09/2013 - 01:40

5% total drop is fine according to GBCI. LEED interpretation ID #10218 confirms it. There is an earlier ruling stating that 2% for feeders must be met but in a response I received from GBCI, the more recent ruling is what counts. I sent an ASHRAE interpretation request about a month ago just for fun. No response from ASHRAE yet.

Mon, 09/09/2013 - 05:55

Very interesting...keep us posted. As to Mr Helmy's problem, my opinion is that unless "emergency" operation is part of the yearly routine running of the building, that it is not required, as it does not effect the annual energy consumption of the building. However, if you mean systems that cover peak energy consumption periods, then yes, the standard applies.

Tue, 11/05/2013 - 16:00

Got a response from ASHRAE. It's posted on their website. ASHRAE says that the 2% and 3% requirements cannot be exceeded individually. I just sent GBCI the ASHRAE ruling to see if they change their position on voltage drop. Funny stuff. https://www.ashrae.org/standards-research--technology/standards-interpretations/interpretation-for-standard-90-1-2007. It's Interpretation 90.1-2007-23 – October 18, 2013 at the bottom of the page. It's on the second page, Interpretation number 5.

Sun, 01/12/2014 - 08:41

I sent an unofficial interpretation request to ASHRAE to ask about the above issue and they replied as follows: No, the requirements in 90.1-2007 are specific as to the 2% and 3% limits and do not make any allowances for emergency circuits. However, the 90.1-2010 version of the standard offers an exemption for emergency circuits that was put in to address these types of issues. You may be able to apply this more recent provision in the 2010 version if the local building authority will accept a more recent version of the standard as more progressive and applicable. therefore is it possible to apply a more recent version (2010 version) of a standard mentioned in LEED v2009 although the mentioned version is the 2007 one? While note that the project is registered as LEED v2009 project

Mon, 01/13/2014 - 13:50

You are allowed to use any addenda to 90.1-2007. Not sure if that change was in an addenda but many of the changes to 90.1 in 2010 came from the addenda. If the change was not in an addenda but it provides clarity where it did not exist before you could also probably use it.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.