FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

ASHRAE 90.1-2007, 6.5.3.1.1,exception b

Greetings, According to ASHRAE 90.1-2007, 6.5.3.1.1,exception b, individual exhaust fans with motor nameplate kW of 0.75 kW or less could be excluded when estimating Fan system power limitation. There are projects however, where there are such small fans, but they are part of some systems - say small 100% OA supply AHUs with only a supply fan and the small fans are the exhaust part of these systems. The question is: Should the power of these small fans (exception b) in the above cases be excluded (taken off) from the fan power calculation performed by the simulation software, or with other words, shall we enter these small fans in the energy model? Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sun, 02/12/2017 - 20:40

The Proposed is always modeled as designed. The baseline fans are modeled according to G3.1.2.9. If a fan is part of the HVAC system then it is covered. If a fan is not part of the HVAC system then it is not regulated and considered a process load. The size of the fan does not matter. That exception would apply for code compliance - those small fans do not have to comply with this prescriptive requirement.

Mon, 02/13/2017 - 06:02

Thanks Marcus, It was very useful explanation.