Hi,
Our problem is with PTHP (cooling mode) new construction.
The footnote 'c' is bit confusing. According to the footnote, the capacity should be in KW and some publish documents say it should in Btu/hr.
Can anyone help us to resolve this issue.
Regards,
KC
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5921 thumbs up
November 8, 2013 - 10:13 am
Are you using the SI or IP version? My IP version says BTU/h.
Keerthi Ratnayake
Managing DirectorEnviron Pvt. Ltd
38 thumbs up
November 10, 2013 - 12:40 am
Hi Marcus,
This is SI edition. The equation is 3.60-(0.213*Cap/1000). If the input is in kW, we believe, deviding the Cap by 1000 is not required.
Any idea?
Regards,
KC
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5921 thumbs up
November 12, 2013 - 9:39 am
I just saw you were asking about 90.1-2004? This version of the standard does not apply to LEED 2009 projects. So you might want to check the 2007 version of the standard and any addenda which may apply. If this is an error I am sure it was caught by now. The results of the calculation should be pretty obvious as the COP should be a single digit number. You could check it against the IP version formula - 12.5-(0.213*cap/1000) EER. COP = EER/3.412