ASHRAE 62.1 Item 5.9 - Minimum filtration required

Is it required to meet the filtration requirement of ASHRAE 62.1-2007, item 5.9 for equipment areas with no occupation?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/15/2012 - 17:17

If it has a cooling coil or wetted surface then yes.

Wed, 08/15/2012 - 18:16

Thanks Andrew, but reading the section 5.9 properly, which says “MERV of not less than 6 when rated in accordance with ANSI/ASHRAE Standard 52.2 shall be provided upstream of all cooling coils or other devices with wetted surfaces through which air supplied to an occupiable space”, I realized that only occupiable space needs to comply with this item.