FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

AREA CRITERIA

HI, I HAVE A PROJECT IN MEXICO CITY, AND THE OWNER DEFINE THE CRITERIA OF DONT USE TREATMENT PLANT AND USE AIR COOLED CHILLERS. THE CONDITIONED AREA IS 130,000 FT2 WITH 9 LEVELS OF OFFICE TOWER. ACCORDING WITH APPENDIX G TABLE G3.1.1A AND G3.1.3.7, FOR NON RESIDENTIAL AND MORE THAN 5 FLOORS OR > 150,000 FT2. THE SYSTEM IN BASE BUILDING IS WATER COOLED CHILLERS. IS CORRECT THIS CRITERIA FOR BASE BUILDING OR I CAN USE IN BASE BUILDING AIR COOLED CHILLERS? THANKS AND REGARDS

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 09/28/2011 - 02:15

Table G3.1.1A defines the baseline HVAC system. Based on your criteria you cannot use air cooled chillers. Make sure to check the exceptions in G3.1.1 to see if any apply.