FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Are there any trade off if using the Existing chiller

Hi all,

The project is an industrial buildings

The project uses Water cooled Centrifugal chiller which is an existing one and relocated from another country to be fitted for a New industrial Building in India. Are there any  trade off in terms of COP as existing COP is 5.8 Further The total HVAC Load is 400 Tonnes, and the chiller capacity 2 no's 300 Tonnes

So in this case kindly advice.

Thanks in advance

Sriram tetali

 

 

 

 

 

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 12/06/2017 - 14:25

Once you relocate a chiller to a new facility it comes under the same 90.1 requirements as a new chiller. So the efficiency must meet the minimum values in Table 6.8.1c. This type of chiller over 300 tons has a minimum efficiency of 6.1 COP. This is a mandatory provision. If you can't meet this mandatory provision the project is not eligible for LEED certification as it can't meet this prerequisite.