Are 30% and 40% PG considered as refrigerant

Hi all, For a new construction project, the fan coil unit schedule shows that the fluid for the cooling coil is 30% PG (Propylene Glycol) and that of the heating coil as 40% PG. Should I consider for the equipment for the enhanced refrigerant management? Thank you!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 08/28/2017 - 19:12

Hi Romio, does propylene glycol contribute to global warming or ozone depletion? I can't find any evidence online that it does, but I'd follow up with the equipment manufacturer to see if you can get some additional details.

Tue, 08/29/2017 - 18:04

My understanding is that propylene glycol is not a refrigerant; it's just the working fluid to transfer heat to/from the coil (versus the refrigerant, which undergoes the vapor change process in the Rankine Cycle). We use glycol in radiant heating/cooling systems all the time and its not a refrigerant, but maybe this is a different case (?)

Thu, 02/27/2020 - 18:50

I have 12 units that us 50/50 glycol and water. Should I have the units in the fundamental Refrigerant prerequisite and enhanced refrigerant management credits? My team believes that only the units that are 100%refrigerant should be listed for both Fundamental Refrigerant prerequisite and enhanced refrigerant management credits. Please advise.