FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Appropriate Fenestration U-value for Baseline Model

I can not tell, from either ASHRAE 90.1-2007 or from the LEED User's Manual, what U-value I am supposed to use for the baseline vertical glazing. Each referenced standard states "...match appropriate requirements in Tables 5.5-1 through 5.5-8." In that table there list 4 types of vertical glazing. Let's say I have a building with 40% glass. In the proposed design there is a room with an perimeter wall, but no glass. In the baseline model, I am to arbitrarily add 40% glass to this wall, but I do not know what the appropriate U-value of the glass should be. Am I missing something here? To be more specific, I am in climate zone 5A.

5

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 08/29/2011 - 17:23

For 90.1-2007, the windows for both baseline and proposed are modeled in the same place if the window area is less than 40% of the total wall area for the building. This is usually the case. 90.1-2004 required bands of windows to be placed around the baseline building. This put windows in places on the baseline building where there were none on the proposed. As far as the U-values, use the same category of window as the proposed building. Notes b and c under the table on page 23 (90-1 2007) help clarify. Hope this helps.

Thu, 09/01/2011 - 19:40

"As far as the U-values, use the same category of window as the proposed building" THANK YOU THOMAS, THIS IS WHAT IS MISSED IN EVERY EXPLANATION!!!