FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Appendix G - Type of system

Hi, I have a doubt related to the type of system I should consider in a specific case. I'm working on a project where most of the bulding is served by one type of system. Based on this, I've defined the baseline system. There's a portion of the building which is neither served by the main system nor have an specific system specified. So, based on Table G3.1, item 10, the "cooling system shall be identical to the system modeled in the baseline building system". As the cooling system for this portion is independent of the main system, should I model another baseline system, based in the conditioned area, type of building and heating source? Thanks a lot. Luana

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/04/2012 - 13:00

No. It should be the same system type as your original baseline system. If the HVAC system has not been designed for this area then the proposed is supposed to be identical to the baseline. You can only model secondary system types if one of the exceptions under G3.1.1 applies.

Tue, 09/04/2012 - 14:02

Hi Marcus, Thanks for your answer. The point is that the HVAC system hasn't been design and won't be designed by the owner. It is independent and tenants will design their own system. I've read the exceptions and they do not apply in my case. I was thinking, for example, if I had an area of 100 m2 that doesn't have the project and the baseline system for the whole bulding was a chiller plant, then for the proposed model, this 100 m2 area would be also served by a chiller plant? Isn't it strange? Thanks!

Tue, 09/04/2012 - 15:09

Appendix G has you do all kinds of strange things! So your proposed has no chiller plant I assume. You would need to model an auto-sized chiller (over-sized by 15%) identical to the baseline in the proposed for that space.

Tue, 09/04/2012 - 17:56

Hi Marcus, Ok. So, I'll consider an auto-sized chiller with the same efficiency as the baseline chiller. Thanks!