FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Appendix G - Number and type of chillers

Hi! I have a doubt related to Appendix G, concerning the number and type of chillers and I think you may help me. In item G.3.1.3.7, it is specified that the number and type of chiller for the baseline model are a function of building peak cooling load. In item G.3.1.2.2, it is specified that the baseline's equipment efficiency shall be oversized by 15% (cooling) and by 25% (heating). So, in order to define the number and type of chillers, may I use the oversized capacity or the non- oversized one? Thanks!

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/11/2012 - 18:54

This is a good question! What I have always done is to 1st set the oversizing factors, then perform a simulations with auto-sized equipment, then use the results to determine the number of chillers.

Tue, 09/11/2012 - 21:43

But actually the building cooling load is not affected by the sizing of the equipment!

Wed, 09/12/2012 - 13:13

G3.1.3.7 indicates the size should be based on the peak cooling load which is different than the equipment size as Santiago mentions. So the number and type of chiller should be based on the peak cooling load. The baseline equipment size is then based on the cooling load plus 15%.

Thu, 09/20/2012 - 14:27

Marcus, I ask this because I've asked some ASHRAE members and, at their view (I didn't get a formal interpretation), I shoud select the number and type based on equipment size. Maybe they were not sure as me... =) Do you know if, in the market, people have adopted the methodology you mentioned? Thanks.

Thu, 09/20/2012 - 15:39

The language in the standard clearly says peak cooling load, not final equipment size. The 15% over-sizing is related to equipment capacity, not peak cooling load. The peak load is the load, not the over-sized equipment capacity. This is how we do it in our models and how the LEED reviewers would expect it to be done in our opinion. I do not know how most modelers do it as this information is generally not provided in a LEED review. Anyone else have an opinion on this one?