NC-2009 IEQc4.2:Low-Emitting Materials—Paints and Coatings

Anti-Graffit coating

What is the VOC limit for this ?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 01/14/2014 - 22:01

Rule 1113 Industrial Maintenance (IM) Coatings Max 420 g/lQuick question - is this product being applied on the interior of the building?

Tue, 01/14/2014 - 23:22

yes - both interior and exterior of the building.

Fri, 01/17/2014 - 15:51

As John-David stated, durable anti-graffiti coatings live in the IM category. IM has performance requirements such as chemical resistance and surviving repeated scrubbing or abrasion - both typical for non-sacrificial anti-graffiti coatings. Some manufacturers bend the curve a bit by selling multiple layer systems where each layer is sacrificial, but still call the product an IM coating. Sacrificial coatings designed to be removed by pressure washing or stripping materials and replaced after each tag would not typically be classified as IM coatings. These would live under other categories such as Low Solids if it is less than 1-pound per gallon solids content or Waterproofing Concrete/Masonry Sealer if marketed for use on brick, block or stone and it has additional water repellent characteristics.