FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Alternative Standard to ASHRAE 90.1-2007 Appendix G

We have a project that consists of two connected buildings: an admin building and a factory building. The total area for the buildings is greater than 150,000 sq ft, therefore system 8 applies to the baseline case model. Unfortunately, our proposed system uses air cooled chillers and we are having a hard time achieving the required savings. According to the USGBC, projects outside the U.S. may use an alternative standard to ANSI/ASHRAE/IESNA Standard 90.1-2007 if it is approved by USGBC as an equivalent standard using the process located at www.usgbc.org/leedisglobal. The above link is broken, and we cannot find anything on the USGBC website that gives guidance on alternative standards to ASHRAE 90.1-2007. So my question is, are there any approved alternative standards to ASHRAE 90.1-2007 for international projects? Has anyone successfully submitted an energy model using a different standard? On another note, is it even possible to achieve the required savings, without using water-cooled chillers, if your baseline model uses system 8 - VAV with PFP Boxes? Your feedback is greatly appreciated. -Michael Aghabi

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 02/23/2016 - 13:15

I am not aware of alternative standards. Achieving the savings is possible. Consider that cooling is not the only end use. Moreover, I think that the water cooled chillers of the baseline require an important amount of energy for pumping. What do people having more experience think about this point? Regards

Tue, 02/23/2016 - 14:19

I do not recall an alternative baseline being approved yet. The process is pretty rigorous and requires some in depth modeling studies. It would be well beyond something an individual project team could attempt. You will need to find the minimum savings elsewhere. Quite often manufacturing facilities will need to find energy savings within their process loads. There is an alternative compliance path for manufacturing facilities which can be found here. http://www.usgbc.org/leed-interpretations?keys=10291

Thu, 03/03/2016 - 19:21

We also have had similar problems in projects in Mexico in some areas where water is scarce and has a high amount of minerals, so cooling towers are not installed in HVAC systems because of the high O&M costs. We then try to achieve energy savings in other areas such as fan power consumption, pumping energy and interior lighting. In hot climate areas it can be difficult to achieve the minimum energy savings treshold because cooling is one of the highest end uses, so if your project is still in the version 3 of LEED you can also try to recommend the client to install an on site renewable energy system to achieve the required energy savings. In version 4, however, renewable energy systems cannot be accounted for pre-requisite EAp2, which makes good sense. Good luck!