Forum discussion

CS-2009 WEp1:Water use reduction

Alternative Compliance Path Documentation

I wish to pursue an Alternative Compliance Path for taking account of collected rainwater being used for the toilet and urinal flushing under credit WCp1 and WE3. Should icomplete the template as having 0 flush volume for the WCs and urinals to "trick" the template into Attempting 4 points? as in our case the provision is actually greater than demand. If it was less than 100% i would pro rata this - correct? thanks

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/11/2011 - 15:09

Vivien,I would not reccomend "tricking" the template. The form is asking how much water is used and does not consider what type of water. Even if it is 100% rainwater (which is fantastic!) you're still using that water so conservation is important. I would suggest selecting the "Alternative Compliance Path" in the form and then providing a narrative describing your strategies.

Fri, 11/11/2011 - 15:17

Thank you - I also just foundthis additional water guidance that has been recently updated http://www.usgbc.org/ShowFile.aspx?DocumentID=6493 I can document the calculations as a narrative - but this won't take account of the points actually achieved by using rainwater to achieve >40% - how should i document this on the template so that it takes account of the 4 points in its calculations without - entering 0 as the flush volume?

Fri, 11/11/2011 - 18:01

The LEED online template will not show it correctly. You will sumit your documentation under alternative compliance path. You than also note this under WE c3, so the reviewer sees that you are using rainwater. This is what we did in a recent project and it's also what the GBCI recommended to do. Also make sure to show that the precipitation and tank size are working throughout the year to cover the water demand of your fixtures.