Does the (airflow sensor) need to have any specifications other than the required accuracy (which is 15%) which was mentioned in the study guide?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
John McFarland
Director of OperationsWorkingBuildings, LLC
LEEDuser Expert
43 thumbs up
May 27, 2013 - 12:25 pm
Hi Ahmed,
The accuracy of 15% is the only specified requirement. Here are a few other tips: 1) make sure it's measuring only outdoor air and not mixed air; 2) if its a pitot-tube type airflow sensor make sure it's downstream of filters on the outdoor air otherwise it's likely to get clogged; 3) be mindful that the alarm has to be programmed for 10% off set point so I'd recommend using a sensor at that is at worst 10% accurate (note, this is more accurate than required but I have no idea why the credit requires an alarm at 10% but an accuracy of 15%). Hope this helps.
-John