Hello, we have several projects that are using single zone RTU's with CO2 based demand control ventilation. We have already established through conversations with a LEED Coach that the units need airflow monitors. This is due to the fact that DCV varies the outside air. However, I do not understand how the alarms would work in this setup. The credit requirement is to have an alarm trigger when the OA varies by 15% from design ventilation established by the VRP calculations. If we do this, an alarm would trigger whenever the outside air damper closes because of a drop in CO2. The engineer wants to have it alarm based on the min OA setting, which is lower than design ventilation. Does anyone have experience with this setup?