FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Air cooled chillers and other air cooled equipment.

Question: If I have an air cooled chiller selected at non-ARI conditions that has a full load efficiency of 3.0 COP, does it comply with the minimum efficiency requirement of 2.8 COP from ASHRAE - 90.1, or does it have to be re-selected at 44 leaving water, 95 condensing air temp, and 2.4 gpm/ton? How about other air-cooled equipment and cooling towers?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 12/19/2012 - 15:12

The minimum efficiency requirements are at the test conditions for all the equipment. If the manufacturer cannot supply the performance at the test conditions you will need to make the case that your equipment complies.

Thu, 12/20/2012 - 09:57

We also has this difficulty, as our project is at Asia,. When contacted the international chiller manufacturer, their local assembly chiller does not go for ARI testing, but those in US are. Is not commercially wise to import these equipment across to our project here. We able to find local assembly chiller which has equivalent COP as in ASHRAE requirement but not ARI Tested. Can the manufacturer test report help us to meet EAP2 requirement?

Thu, 12/20/2012 - 21:01

I would most certainly enlist the manufacturer to help you document efficiency compliance. Perhaps the chiller curve could be used to help demonstrate compliance?