We're working on a EBOM building, in which the main space is an indoor arena. There are also support spaces around the main arena, such as offices, gym, yoga rooms, etc.
There are 2 AHUs supplying conditioned air to the main space (with a mix of outdoor air, representing 40%, and return air - 60%).
Since the indoor arena (sports arena or spectators area) is classified as Class 1 air by table 6-1 of ASHRAE 62.1-2010, the building uses the conditioned air of the main space as outdoor air which is supplied to the adjacent support spaces via fans. For the purpose of the OA calculations, we are only taking into account the portion of outdoor air provided by the AHU (40% of total air).
Example: an adjacent office, with its own VRF indoor unit, requires 20 l/s of outdoor air. We understand that it is acceptable to supply 50 l/s of the main arena conditioned air to the office and that this fulfills the 20 l/s OA requirement per ASHRAE. Is our assumption correct?
The total outdoor airflow rate of the 2 AHUs is enough to comply with ASHRAE 62.1-2010 for all spaces together (arena + support spaces).
Is this approach acceptable by LEED?