Since I'm pursuing the prescriptive method of this prerequisite, I am filling out the entire AEDG. For the Daylighting and Lighting section, it asks for interior surface average reflectance in terms of 80% ceilings, 70% wall surfaces, and 50% open office partitions. In order to determine this, can i just sum up the ceilings and wall surfaces in the architecture drawings and make a percentage of the surface area which have a white surface (since white is usually reflective) out of the total surface area?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5927 thumbs up
October 25, 2023 - 12:06 pm
Typically you would use the specific paint color (all paint has a reflectance value) for the walls and for the ceiling tiles (again they have a rated reflectance). If there are mixed surface areas then yes you would take a weighted average. The partition surfaces would also have a reflectance rating.
Edgar Arevalo
Associate19 thumbs up
October 25, 2023 - 3:39 pm
Is the reflectance value for paint colors in % or some other unit? Same goes for the rated reflectance for the ceiling tiles.
Because when the AEDG table says average surface reflectance in %, I can't tell if they mean % of high reflective surface over total surface or if the reflactance is in % so we just take the average of that
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5927 thumbs up
October 25, 2023 - 3:57 pm
Yes both are typically a percentage. It is technically referred to as LRV (Light Reflectance Value). Pure black is 0 and pure white is 100.